I have an ET2.4 and am running njs-PC 8.0.1 and Dashpanel 8.0.0. I also run the HA Integration 0.4.12. Everything has been running flawlessly for months. Because the weather is cooler & my pool is in the shade most of the day, I have been turning down the Intellichlor setting using either/both the HA integration and the Dashpanel. Both report the same setting and output level. However, the chlorine level measured with a test kit has been increasing. This morning I noticed the salt cell had 2 green LEDs for the cell output (40%), even though the setting in Dashpanel is 5%. On the ET itself, the setting shows as 32%. On the ET I lowered the setting to 20% and the salt cell switched to one green LED for the output, which I believe to be correct for 20%. However,, Dashpanel & HA both continue to report a setting and output of 5%. Everything else appears to be correct on the Dashpanel and HA integration: Pump Speed, Water Temperature, Heater Setting, Schedules for the filter pump and booster pump, Filter Pump Speed Setting, etc. I've never noticed this inconsistency in behavior previously. Can you kindly suggest how to troubleshoot, and hopefully correct, this inconsistency? Thanks for your help!!!! |
Beta Was this translation helpful? Give feedback.
Replies: 1 comment 4 replies
-
Actually once you get below 10% the lights switch to ~2% per light or 5%. |
Beta Was this translation helpful? Give feedback.
I no longer run the ET and am full Nixie now :-)
To close the loop, I believe the problem was the RS-485 surge suppressor I installed between the surge board and the ET & njsPC. There's a little more information about my experiences & resolution of trying to get the Intellichlor to communicate with Nixie towards the end of this thread.
#892